After the discussion about the fuel shut offs I did some research in the Code. Here is what it says
24.14.9
Fuel distribution and return systems shall be provided with anti-siphon protection by at least one of the following:
24.14.9.1
Keeping all parts of fuel distribution and return lines above the level of the tank top from the tank to the carburetor inlet or a location where fuel leakage cannot enter the boat when the boat is in its static floating position.
2414.9.2
Installing an anti-siphon device at the tank withdrawal fitting or along the line, with a rated siphon protection head and flow rate greater than required for the installation
24..l4.9.3
Installing an electrically operated valve at the tank withdrawal fitting or along the line connected to be energized open only when the engine ignition switch is on and the engine is runing A momentary type override is acceptable for starting
24.14.94
Installing a manual shut-off valve directly at the fuel tank connection arranged to be readily accessible for operation from outside the compartment if the fuel tank top is located below the level of the carburetor inlet and the fuel line is rigid metal or USCG Type Al hose. If the length of fuel line from the tank outlet to the engine inlet is greater than 12 feet, a second manual shut-off valve shall be installed at the fuel inlet connection to the engine.
So looks like Wolf is correct with a Shut-Off valve. I think I am going to put an Anti Siphon valve on my fuel outlets because I think if you have a fire, or a leak it will stop the flow automatically rater than having to find a valve (If the boats on fire I will be more focused on getting the hell off it...)
With further reading in the Canadian Code it adds this note. Wolf's Surveyor was correct but it could have also been handled by any of the other 3 options
Information Note:
“Readily accessible for operation from outside the compartment” may be achieved by a shut-off valve installed at the tank, close to, and directly below, a quick-acting access port in the deck through which the valve can be operated. The access port shall be clearly and permanently labeled.
I am going to install: http://www.moellermarine.com/moelle...anti-siphon-valve-38-npt-x-38-barb-033808-10/
Since you have an aluminium tank you will want the Aluminium version if you decide go in that direction.
Here is the ABYC Fuel System Code (Gasoline), It a good read!
https://law.resource.org/pub/us/cfr/ibr/001/abyc.H-24.1993.pdf
Also Here is Canadian Code
https://www.tc.gc.ca/eng/marinesafety/tp-tp1332-menu-521.htm#wb115
After the discussion about the fuel shut offs I did some research in the Code. Here is what it says
24.14.9
Fuel distribution and return systems shall be provided with anti-siphon protection by at least one of the following:
24.14.9.1
Keeping all parts of fuel distribution and return lines above the level of the tank top from the tank to the carburetor inlet or a location where fuel leakage cannot enter the boat when the boat is in its static floating position.
2414.9.2
Installing an anti-siphon device at the tank withdrawal fitting or along the line, with a rated siphon protection head and flow rate greater than required for the installation
24..l4.9.3
Installing an electrically operated valve at the tank withdrawal fitting or along the line connected to be energized open only when the engine ignition switch is on and the engine is runing A momentary type override is acceptable for starting
24.14.94
Installing a manual shut-off valve directly at the fuel tank connection arranged to be readily accessible for operation from outside the compartment if the fuel tank top is located below the level of the carburetor inlet and the fuel line is rigid metal or USCG Type Al hose. If the length of fuel line from the tank outlet to the engine inlet is greater than 12 feet, a second manual shut-off valve shall be installed at the fuel inlet connection to the engine.
So looks like Wolf is correct with a Shut-Off valve. I think I am going to put an Anti Siphon valve on my fuel outlets because I think if you have a fire, or a leak it will stop the flow automatically rater than having to find a valve (If the boats on fire I will be more focused on getting the hell off it...)
With further reading in the Canadian Code it adds this note. Wolf's Surveyor was correct but it could have also been handled by any of the other 3 options
Information Note:
“Readily accessible for operation from outside the compartment” may be achieved by a shut-off valve installed at the tank, close to, and directly below, a quick-acting access port in the deck through which the valve can be operated. The access port shall be clearly and permanently labeled.
I am going to install: http://www.moellermarine.com/moelle...anti-siphon-valve-38-npt-x-38-barb-033808-10/
Since you have an aluminium tank you will want the Aluminium version if you decide go in that direction.
Here is the ABYC Fuel System Code (Gasoline), It a good read!
https://law.resource.org/pub/us/cfr/ibr/001/abyc.H-24.1993.pdf
Also Here is Canadian Code
https://www.tc.gc.ca/eng/marinesafety/tp-tp1332-menu-521.htm#wb115